Subject Topic: Modbus RTU turn around time must be 1mS Post Reply Post New Topic
Message posted by Budd on 20 December 2008 at 12:43am - IP Logged
View Budd's Profile Search for other posts by Budd Quote Budd Send Private Message Add to Buddy List
Budd
Avatar
Standard Member
Standard Member
United States
07 September 2006
29 Posts

The RS-485 Modbus RTU connection between a Honeywell XYR 5000 base station (Modbus slave)and a Honeywell Trendview recorder (Modbus Master) requires that the turn around time setting for the RS-485 on the Trendview recorder be 1mS, not the default 3mS.  

Experience shows that the default 3mS setting gets less than 1% of the responses from the XYR base station; producing a very intermittent, fault and error prone Modbus link.   The 1mS setting runs perfectly, with zero errors.

Budd